coffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shed
 
coffeesnob's Avatar
Joined: Feb 2010, #30892
Location: VA
Gender: Male
Posts: 1,544
coffeesnob's Tacoma Gallery
GFI keeps tripping

The GFI in my garage keeps tripping. When it trips a red light on it comes on. Sometimes it trips right away other times it takes a few seconds. I know nothing about electricity but if you think this is a bad GFI I can replace it myself... Thanks
  Reply With Quote
Old 11-23-2010, 01:01 PM   #2
Mad Fisherman
DaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shed
 
DaCapt's Avatar
Name: Phil
Joined: Apr 2010, #35429
Location: Old Station,Calif.
Gender: Male
Posts: 496
DaCapt's Tacoma Gallery
is it a wall gfi or a gfi in the electrical box?
  Reply With Quote
Old 11-23-2010, 01:10 PM   #3
Senior Member
Snipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shedSnipe is one of the sharper tools in the shed
Joined: Jan 2009, #12421
Location: Pacific NW
Gender: Male
Posts: 1,156
Snipe's Tacoma Gallery
Start with unplugging anything down line of the GFI, the problem item doesn't need to be plugged directly into that outlet, it just needs to be on that line and triggering the GFI into seeing a ground fault.
  Reply With Quote
Old 11-23-2010, 01:29 PM   #4
Crash and burn live and learn
Hugebergen will become famous soon enoughHugebergen will become famous soon enough
 
Hugebergen's Avatar
Joined: Feb 2010, #30927
Location: Saskatoon Sask
Gender: Male
Posts: 100
Hugebergen's Tacoma Gallery
If the GFI is on the same circuit as the lights it can cause it to trip. Theres nothing plugged into it when it trips?
  Reply With Quote
Old 11-23-2010, 02:22 PM   #5
coffeesnob [OP] coffeesnob is offline
Senior Member
coffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shed
 
coffeesnob's Avatar
Joined: Feb 2010, #30892
Location: VA
Gender: Male
Posts: 1,544
coffeesnob's Tacoma Gallery
Quote:
Originally Posted by DaCapt View Post
is it a wall gfi or a gfi in the electrical box?
all
the gfi is in a wall. It trips on its own.. the only thing plugged into down stream ( I think) is an extension cord with a multi strip deal on it that is turned off. I've only had a battery charger plugged into the multi outlet strip so I don't think it is causing an overload. One other thing may be a coincidence. I had my house pressure washed today and the circuit breaked box is outside on the house. I am wondering if mositure got in it. It should have dried by now though
  Reply With Quote
Old 11-23-2010, 02:32 PM   #6
Mad Fisherman
DaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shedDaCapt is one of the sharper tools in the shed
 
DaCapt's Avatar
Name: Phil
Joined: Apr 2010, #35429
Location: Old Station,Calif.
Gender: Male
Posts: 496
DaCapt's Tacoma Gallery
yep, that would be a good reason it tripped. If this is the first time it has given you problems, then yes it was the power wash. Let it dry out on its own, or give it a blow dry, either using a compressor , or when its dry outside, you can use a hair dryer. Take the faceplate off before you try either method. Also might help to turn off that circuit, before you attempt to dry the outlet.
  Reply With Quote
Old 11-23-2010, 02:35 PM   #7
Famous Fabrication
DWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shedDWreck is one of the sharper tools in the shed
 
DWreck's Avatar
Name: Derek
Joined: May 2010, #37368
Location: Las Vegas, NV
Age: 26
Gender: Male
Posts: 5,849
DWreck's Tacoma Gallery
Sounds like ur equip has an issue
__________________
Click Sig Pic Click Sig Pic Click Sig Pic Click Sig Pic Click Sig Pic
  Reply With Quote
Old 11-23-2010, 02:37 PM   #8
Senior Member
WNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shed
Joined: Nov 2008, #10961
Location: Clarence, New York
Gender: Male
Posts: 1,335
WNYTACOMA's Tacoma Gallery
Quote:
Originally Posted by coffeesnob View Post
all
the gfi is in a wall. It trips on its own.. the only thing plugged into down stream ( I think) is an extension cord with a multi strip deal on it that is turned off. I've only had a battery charger plugged into the multi outlet strip so I don't think it is causing an overload. One other thing may be a coincidence. I had my house pressure washed today and the circuit breaked box is outside on the house. I am wondering if mositure got in it. It should have dried by now though
A lot of times, the garage interior wall will reset the exterior outlets on the same circuit, so it could be related...

I would give it a chance to 'dry out' and see it that takes care of it. In the future, you might want to tape over / seal the exterior outlets prior to another power wash.
  Reply With Quote
Old 11-23-2010, 02:37 PM   #9
coffeesnob [OP] coffeesnob is offline
Senior Member
coffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shed
 
coffeesnob's Avatar
Joined: Feb 2010, #30892
Location: VA
Gender: Male
Posts: 1,544
coffeesnob's Tacoma Gallery
Quote:
Originally Posted by DaCapt View Post
yep, that would be a good reason it tripped. If this is the first time it has given you problems, then yes it was the power wash. Let it dry out on its own, or give it a blow dry, either using a compressor , or when its dry outside, you can use a hair dryer. Take the faceplate off before you try either method. Also might help to turn off that circuit, before you attempt to dry the outlet.

The gfi is in my garage and dry as a bone. I menat that the breaker box was outside.
  Reply With Quote
Old 11-23-2010, 02:47 PM   #10
Member
davidsdad will become famous soon enough
 
davidsdad's Avatar
Name: Dave
Joined: Jul 2010, #40383
Location: Grove City, Ohio
Age: 47
Gender: Male
Posts: 64
davidsdad's Tacoma Gallery
Unplug the poower strip and all other equipment on this circuit and then attempt to re-set the G.F.C.I. If then it resets you know one of the items plugged into this circuit is causing the ground fault!! Let us know how it turns out!!!
__________________
Just Passin Thru!!
  Reply With Quote
Old 11-23-2010, 02:49 PM   #11
Senior Member
macgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shed
 
macgyver's Avatar
Name: Brad
Joined: Aug 2009, #21173
Location: Canton, GA
Gender: Male
Posts: 3,546
macgyver's Tacoma Gallery
the gfci outlet may be in your garage but it could control outlets on the outside. mine does in my house.
  Reply With Quote
Old 11-24-2010, 04:17 AM   #12
coffeesnob [OP] coffeesnob is offline
Senior Member
coffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shed
 
coffeesnob's Avatar
Joined: Feb 2010, #30892
Location: VA
Gender: Male
Posts: 1,544
coffeesnob's Tacoma Gallery
Quote:
Originally Posted by davidsdad View Post
Unplug the poower strip and all other equipment on this circuit and then attempt to re-set the G.F.C.I. If then it resets you know one of the items plugged into this circuit is causing the ground fault!! Let us know how it turns out!!!

Its still is tripping. If I get a chance I am going to the hardware store and buy a new outlet and go from there...thx
  Reply With Quote
Old 11-24-2010, 04:38 AM   #13
:POOPCORN:
98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed98tacoma27 is one of the sharper tools in the shed
 
98tacoma27's Avatar
Marines:
Name: Ben
Joined: Dec 2008, #11714
Location: Beech Creek
Gender: Dude
Posts: 53,451
98tacoma27's Tacoma Gallery
Quote:
Originally Posted by coffeesnob View Post
Its still is tripping. If I get a chance I am going to the hardware store and buy a new outlet and go from there...thx
I think you are wasting your time buying a new outlet. A GFI monitors the load on both sides (hot and common/neutral). A wet neutral line (or even ground since they are typically bonded at the box) could cause it to trip. And as others have said, an exterior outlet or the main box itself could have moisture in it which could take a few days to dry out. I'd say give it a week and see what happens. Pressure washing can force water into unwanted places.
__________________
Quote:
Originally Posted by Martie View Post
I think it's going to be thick pastrami on rye with swiss, coleslaw, bacon, and russian dressing. .
Quote:
That’s no reason to cry. One cries because one is sad. For example, I cry because others are stupid, and that makes me sad.
  Reply With Quote
Old 11-24-2010, 05:10 AM   #14
Senior Member
Dimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shedDimonback is one of the sharper tools in the shed
Name: Patrick
Joined: Mar 2010, #32964
Location: Austin, Tx, from all over hell and back
Gender: Male
Posts: 820
Dimonback's Tacoma Gallery
It's likely that the GFI is working correctly, and as someone else pointed out, one of the other exterior receptacles has faulted due to the power wash. Shack electricians will typically use one GFI to power several receptacles downline to save money. Check your exterior recepts before you buy a new GFI.
  Reply With Quote
Old 11-24-2010, 05:22 AM   #15
Senior Member
WNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shedWNYTACOMA is one of the sharper tools in the shed
Joined: Nov 2008, #10961
Location: Clarence, New York
Gender: Male
Posts: 1,335
WNYTACOMA's Tacoma Gallery
Quote:
Originally Posted by Dimonback View Post
It's likely that the GFI is working correctly, and as someone else pointed out, one of the other exterior receptacles has faulted due to the power wash. Shack electricians will typically use one GFI to power several receptacles downline to save money. Check your exterior recepts before you buy a new GFI.
Yep.

If you have a circuit fed by your service equipment ('main panel') on a grounded circuit, the GFCI outlet closer to the source (panel) will (or should) provide GFCI protection for the outlets farther away or 'downstream'.

In other words, you don't have to see the little buttons on the outlet for them to be GFCI protected, and in your case, it sounds like the GFCI outlet closer to the panel is the one in the garage interior wall, whether it be on the garage / house common wall or possibly the rear wall. That one would 'reset' the exteriors, in all likelihood, in your case.

Let it 'dry out' for some days and see if that takes care of it, otherwise, you might have to target the effected outlet.
  Reply With Quote
Old 11-24-2010, 05:23 AM   #16
Denting the bacon
xJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shedxJuice is one of the sharper tools in the shed
 
xJuice's Avatar
Name: Josh
Joined: Oct 2007, #3208
Location: North DFW
Age: 30
Gender: Male
Posts: 5,621
xJuice's Tacoma Gallery
I've had a similar issue. My GFCI in my garage was randomly tripping itself. It's connected to the 3 exterior outlets on my house also. The seals around the ext. outlets (between the plate and brick) weren't very good so I figured that maybe water was getting behind them when it rained. Two of the outlets are uncovered. Caulked a nice silicone seal around them and also around my back patio light fixture. Haven't had a problem since. (knock on wood)
__________________

If all you're goin' on is my confession, forget it, I'm simply not credible.
Quote:
Originally Posted by OZ-T View Post
Damn you and your fancy USA
  Reply With Quote
Old 11-24-2010, 05:25 AM   #17
coffeesnob [OP] coffeesnob is offline
Senior Member
coffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shedcoffeesnob is one of the sharper tools in the shed
 
coffeesnob's Avatar
Joined: Feb 2010, #30892
Location: VA
Gender: Male
Posts: 1,544
coffeesnob's Tacoma Gallery
Quote:
Originally Posted by 98tacoma27 View Post
I think you are wasting your time buying a new outlet. A GFI monitors the load on both sides (hot and common/neutral). A wet neutral line (or even ground since they are typically bonded at the box) could cause it to trip. And as others have said, an exterior outlet or the main box itself could have moisture in it which could take a few days to dry out. I'd say give it a week and see what happens. Pressure washing can force water into unwanted places.
I'll take that advice. I'll Give it a week and see what happens and thanks all. and happy thanksgiving
  Reply With Quote
Old 11-24-2010, 05:26 AM   #18
Senior Member
macgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shed
 
macgyver's Avatar
Name: Brad
Joined: Aug 2009, #21173
Location: Canton, GA
Gender: Male
Posts: 3,546
macgyver's Tacoma Gallery
Quote:
Originally Posted by Dimonback View Post
It's likely that the GFI is working correctly, and as someone else pointed out, one of the other exterior receptacles has faulted due to the power wash. Shack electricians will typically use one GFI to power several receptacles downline to save money. Check your exterior recepts before you buy a new GFI.
There's actually nothing wrong with using one GFCI to power multiple downline receptacles as long as you don't exceed the maximum wattage and amperage the breaker allows which by standard practice is around 80% of the breakers rating. Show me where in the NEC that says this is unacceptable?
  Reply With Quote
Old 11-24-2010, 05:29 AM   #19
Senior Member
tacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shedtacomatrd99 is one of the sharper tools in the shed
 
tacomatrd99's Avatar
Name: Mike
Joined: May 2010, #37191
Location: Union County, NJ
Age: 31
Gender: Male
Posts: 1,998
tacomatrd99's Tacoma Gallery
I had this problem when I bought my house a few years ago. Anytime it rained, my GFI tripped. Looked everywhere for an answer. Turned out the caulk around the lights on my back porch had a small hole in it and was letting water in. My house was built in '42 so all the GFI and exterior sockets are on one circuit. I never thought to look at the lights because they're not plugged in (hardwired).
__________________
"The world meets nobody half-way. If you want something, you've gotta take it."

"You couldn't be more full of shit if you ate a bag of fertilizer."
  Reply With Quote
Old 11-24-2010, 05:40 AM   #20
Senior Member
macgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shedmacgyver is one of the sharper tools in the shed
 
macgyver's Avatar
Name: Brad
Joined: Aug 2009, #21173
Location: Canton, GA
Gender: Male
Posts: 3,546
macgyver's Tacoma Gallery
Quote:
Originally Posted by coffeesnob View Post
I'll take that advice. I'll Give it a week and see what happens and thanks all. and happy thanksgiving
Mine did their job last year. I had the christmas lights on the bushes plugged in and everytime my dog would pee on the bushes it will trip the circuit. A little bit of "liquid" on the circuit can trip it.
  Reply With Quote