1. Welcome to Tacoma World!

    You are currently viewing as a guest! To get full-access, you need to register for a FREE account.

    As a registered member, you’ll be able to:
    • Participate in all Tacoma discussion topics
    • Communicate privately with other Tacoma owners from around the world
    • Post your own photos in our Members Gallery
    • Access all special features of the site

Home Improvement Today?

Discussion in 'Garage / Workshop' started by Hotdog, Jul 28, 2008.

  1. Oct 31, 2023 at 8:23 AM
    Fargo Taco

    Fargo Taco Well-Known Member

    Joined:
    Mar 14, 2020
    Member:
    #322125
    Messages:
    8,931
    Gender:
    Male
    First Name:
    Not Drew but still Drew
    Fargo
    Vehicle:
    2019 TRD Pro
    Lomax tonneau cover, N-Fab Podium steps, bed mat
    The way you described it - turning the box around to make it an exterior receptacle - anything that's wired in down stream would be protected, for better or for worse.

    If everything was pulled back to a junction box and the now exterior receptacle was tied off of that, it wouldn't shut anything down besides itself.
     
  2. Oct 31, 2023 at 8:31 AM
    daveeasa

    daveeasa FBC Harness Solutions

    Joined:
    May 14, 2020
    Member:
    #328079
    Messages:
    7,479
    Gender:
    Male
    First Name:
    David
    PNW
    Vehicle:
    2016 Tacoma OR DCSB 6MT, 2005 RC 5MT PreRunner, 2002 Tundra SR5 RCLB 4x4
    Why do the other boxes on the circuit need to be on the load / downstream. That is my question. I don’t see why that is necessary but maybe that’s code? Anything entering a box with gfci must be protected downstream?

    my suggestion was make the box serve two purposes.
    1. Junction box
    2. Outside power (needs gfci and waterproof plate.)
     
  3. Oct 31, 2023 at 8:50 AM
    TacoMTga

    TacoMTga Well-Known Member

    Joined:
    Jul 13, 2018
    Member:
    #259242
    Messages:
    1,069
    Gender:
    Male
    First Name:
    Brian
    You can put a gfci in with the line and load wires connected to the line side of the receptacle and not protect whats downstream provided the load down circuit doesnt require gfci protection
     
    98tacoma27 and daveeasa[QUOTED] like this.
  4. Oct 31, 2023 at 10:36 AM
    Toyko Joe

    Toyko Joe Here for the pictures

    Joined:
    Sep 19, 2014
    Member:
    #138654
    Messages:
    5,288
    I’ve never heard of such nor have I came across in any of my code book readings.

    I have a few throughout my house directly under windows and the house is only 5 years old so…

    Some AHJ might require it but it would need to be explicitly stated.
     
    wilcam47 and soundman98 like this.
  5. Oct 31, 2023 at 10:38 AM
    Delta09

    Delta09 Requires Supervision

    Joined:
    Apr 29, 2019
    Member:
    #291677
    Messages:
    13,302
    Gender:
    Male
    First Name:
    Adam
    South Central PA
    Vehicle:
    2024 SR5 DCSB 4WD
    This is why I ended the sentence with a question mark. Trying to remember what electrician told me that.
     
    wilcam47 likes this.
  6. Oct 31, 2023 at 10:44 AM
    Pablo8

    Pablo8 Here!

    Joined:
    Aug 7, 2019
    Member:
    #301483
    Messages:
    9,859
    Gender:
    Male
    First Name:
    Paul
    Everson WA
    Vehicle:
    2019 Cement Sport 4X4 MT AC
    OVT, 4.88, ADM, F&R ARB lock, KO2's, RWD L MOD
    I'm looking at three plugs under windows in my office. It's not a national code thing.
     
    shakerhood and wilcam47 like this.
  7. Oct 31, 2023 at 11:10 AM
    MGMDesertTaco

    MGMDesertTaco Come on, live a little...

    Joined:
    Jan 30, 2021
    Member:
    #354573
    Messages:
    10,448
    Gender:
    Male
    I'm not aware of any code that states you can't have outlets above or below windows. I know there are spacing requirements, a minimum number required for rooms and I think recommendations for height requirements. 18" - 48" I think?
     
    wilcam47 and soundman98 like this.
  8. Oct 31, 2023 at 12:15 PM
    theesotericone

    theesotericone Well-Known Member

    Joined:
    Jul 27, 2018
    Member:
    #260800
    Messages:
    12,378
    Gender:
    Male
    Bishop CA
    There's no code about placements of outlets except in kitchens and baths near water sources. The NEC as far as I know doesn't even have a code requirement for height of outlet or switches. Basically you can put them wherever the fuck you want but 18 for outlets and 48 for switches is the standard most electricians use.
     
  9. Oct 31, 2023 at 1:51 PM
    TacoMTga

    TacoMTga Well-Known Member

    Joined:
    Jul 13, 2018
    Member:
    #259242
    Messages:
    1,069
    Gender:
    Male
    First Name:
    Brian
    Kitchen countertops, rec must be no more than 4’ apart and other room must have receptacles no more than 12 ft apart
     
  10. Nov 1, 2023 at 5:18 PM
    soundman98

    soundman98 Well-Known Member

    Joined:
    May 31, 2021
    Member:
    #367288
    Messages:
    6,167
    Gender:
    Male
    NW Indiana
    Vehicle:
    '18 Taco Sport, '14 Ranger
    happy halloween! i would've chimed in sooner, but was busy throwing candy at kids!

    yes, it's a mega-quote, because info is everywhere except where it needs to be...

    those would be my initial 2 options.

    2 further options

    3. move it up and to the left of the picture. it would be more out of the way, and still be accessible. i've put outlets like that up in the corner and had the painters paint over the cover plate before in situations where i lacked access(ie. they didn't want to pay to cut open the ceiling, and have it repainted) above the ceiling, but they still wanted the outlet moved.
    4. if there's enough wire, sometimes it can be pulled and re-installed via the attic in an existing light fixture box-- saves the zombie junction boxes in the attic, still remains accessible. but still requires attic work.

    just to clarify, because i've seen it done-- drill through the vertical 2x4's at least 6" below the window sill. running in the gap underneath the window while feasible, is a really crappy way to kill a window replacement guy. and technically not to code, as it's not protected from damage. along this line, note that the wire must be ran in the middle of the 2x4. if it's not centered, nail plates must be installed to protect it from damage.

    i don't know of any code for outlets that specify that.

    air conditioners generally aren't installed under windows due to the noise permability, but that's a general rule of thumb that some ahj's enforce, not a code.

    only if wired as such. it's very easy to wire the gfi to only protect itself, and then a splice behind it would maintain the circuit integrity to any other outlets on the same breaker.

    not at all. but i've always considered it unfriendly to do if there's a problem, as outside boxes are inherently moisture-prone, which increases the chance the splice will deteriorate over time, and no one is going to first check an outside outlet for a problem that they're most likely to first complain about from inside a room, meaning that when it fails, it's going to piss off the homeowner after they get the rather large bill to hunt it down.

    there is minimum spacing requirements--bedrooms and general-use rooms are 6' from any door/closet/break in the wall, and 12' measured along the wall after that, hallways only require 1 outlet if they're over 10' long, and garage's only require 1 outlet per vehicle stall) there's also countertop spacing standards-- 2' from the edge/wall, every 4' after that, 9" cabinet minimum still requires an outlet though.

    there is a minimum recommended based on a calculation of the volt-amps-per-square-feet of the house, but i've never had to calculate it outside of apprentice class, as the typical 6'/12' and 2'/4' rules get close enough no ahj has an issue with it.

    but there's no official heights required by the NEC. general rule of thumb is around 15-20" for wall outlets, and switches are generally 45-52". ADA Compliance has some more specific requirements that i know enough to know of, but don't know the specifics of.
     
  11. Nov 1, 2023 at 6:20 PM
    jjones.yota

    jjones.yota Well-Known Member

    Joined:
    Sep 1, 2020
    Member:
    #339479
    Messages:
    2,710
    Gender:
    Male
    First Name:
    Jack
    This guy, is not a dummy like me :rofl:
     
  12. Nov 2, 2023 at 12:06 PM
    Sig45

    Sig45 Well-Known Member

    Joined:
    Jun 21, 2012
    Member:
    #81045
    Messages:
    23,771
    Gender:
    Male
    First Name:
    Mark
    Maine
    Vehicle:
    2011 Tacoma TRD OR DC 4x4 & 2021 Tundra SR5 DC 4x4
    Made it back to that deck project to install the railing on that short angled section and wrap the rim joist with Azek. Ended up using a different brand of railing that had adjustable angle brackets. Can hardly tell the difference and certainly can't tell from the ground. Customer is very pleased.

    [​IMG]
    [​IMG]
     
  13. Nov 2, 2023 at 5:08 PM
    soundman98

    soundman98 Well-Known Member

    Joined:
    May 31, 2021
    Member:
    #367288
    Messages:
    6,167
    Gender:
    Male
    NW Indiana
    Vehicle:
    '18 Taco Sport, '14 Ranger
    meh, when you do something like electrical for 13 years, one tends to pick up on a few things!
     
  14. Nov 2, 2023 at 7:05 PM
    theesotericone

    theesotericone Well-Known Member

    Joined:
    Jul 27, 2018
    Member:
    #260800
    Messages:
    12,378
    Gender:
    Male
    Bishop CA
    What's the code say about cover plate screws? Horizontal or vertical? lol

    The answer is match the longest run of the cover plate. So vertical for single gang, dealers choice for double gang, and horizontal for triple gang. Didn't we have this debate last year in this very thread? lol
     
  15. Nov 2, 2023 at 10:15 PM
    OZ-T

    OZ-T I hate my neighbour

    Joined:
    Dec 15, 2009
    Member:
    #27584
    Messages:
    50,587
    Gender:
    Male
    First Name:
    Peter North
    British Columbia
    Vehicle:
    Mag Grey 09 Trd Sport DCLB 4x4
    OME 885x , OME shocks and Dakars , Wheelers SuperBumps front and rear , 275/70/17 Hankook ATm , OEM bed mat , Weathertech digifit floor liners , Weathertech in-channel vents , headache rack , Leer 100RCC commercial canopy , TRD bedside decals removed , Devil Horns by Andres , HomerTaco Satoshi
    vertical always

    unlike wall plywood which should always be horizontal , stupid California
     
  16. Nov 3, 2023 at 6:31 AM
    theesotericone

    theesotericone Well-Known Member

    Joined:
    Jul 27, 2018
    Member:
    #260800
    Messages:
    12,378
    Gender:
    Male
    Bishop CA
    LMAO.

    10' OSB has a strength axis. It's gotta be vertical if used as sheer. That's not true of 8' OSB or ply so it can be run either way. lol
     
    Pablo8 likes this.
  17. Nov 3, 2023 at 6:41 AM
    Pablo8

    Pablo8 Here!

    Joined:
    Aug 7, 2019
    Member:
    #301483
    Messages:
    9,859
    Gender:
    Male
    First Name:
    Paul
    Everson WA
    Vehicle:
    2019 Cement Sport 4X4 MT AC
    OVT, 4.88, ADM, F&R ARB lock, KO2's, RWD L MOD
    Never messed with 10' OSB but I didn't know that.

    I went vertical on the first wall in my shop with 1/2" (15/32") plywood. Because it fit and less cutting! It's been 1.5 years. Nothing has fallen or collapsed. So there!
     
  18. Nov 3, 2023 at 6:42 AM
    theesotericone

    theesotericone Well-Known Member

    Joined:
    Jul 27, 2018
    Member:
    #260800
    Messages:
    12,378
    Gender:
    Male
    Bishop CA
    I'd love to be able to run sheer horizontally. It's so much easier. lol
     
    Pablo8[QUOTED] likes this.
  19. Nov 3, 2023 at 7:29 AM
    OZ-T

    OZ-T I hate my neighbour

    Joined:
    Dec 15, 2009
    Member:
    #27584
    Messages:
    50,587
    Gender:
    Male
    First Name:
    Peter North
    British Columbia
    Vehicle:
    Mag Grey 09 Trd Sport DCLB 4x4
    OME 885x , OME shocks and Dakars , Wheelers SuperBumps front and rear , 275/70/17 Hankook ATm , OEM bed mat , Weathertech digifit floor liners , Weathertech in-channel vents , headache rack , Leer 100RCC commercial canopy , TRD bedside decals removed , Devil Horns by Andres , HomerTaco Satoshi
    I'll let my structural engineer and the rest of North America know
     
  20. Nov 3, 2023 at 7:35 AM
    Pablo8

    Pablo8 Here!

    Joined:
    Aug 7, 2019
    Member:
    #301483
    Messages:
    9,859
    Gender:
    Male
    First Name:
    Paul
    Everson WA
    Vehicle:
    2019 Cement Sport 4X4 MT AC
    OVT, 4.88, ADM, F&R ARB lock, KO2's, RWD L MOD
    Considering the sheer strength is provided on the outside wall, I'm only moderately worried and there was only insulation - no drywall, nothing on the inside, yeah just kidding about worrying!
     

Products Discussed in

To Top